Need some help with some compressor wiring. Was given a compressor as a backup. Its wired for 220V operation need to figure out how to re-wire it for 110 V besides the plug anyone know what wire change would be required? There is an additional Thumbnail photo that I had trouble uploading that shows more info

Thanks BIG
20180510_142547.jpg


20180510_142735.jpg
 
You should assume the current will double. If that's 12 ga. wire; you probably want 10 ga; that is, go to the next lower gauge (heavier) wire.
 
Does the motor nameplate list dual voltages ie 110/220 ?. What are the amperage's listed at those values. There are certain motors that can not run on dual voltages.

Dave
 
Man my eyes are terrible. Hard to make out the colors on diagram but with a million mega magnifying glass

6 (Brown) moves to 2
2( White ) moves to 4
1 will be incoming 120 Black
4 will be incoming White (Neutral)
You have a 20 amp circuit I presume

Dave
 
DAVE YOU ARE THE MAN!!!!!

Moved the wires to new locations installed the new plug it in WORKS !!!!

I owe you a 6 pack or two.

Thanks Pard
 