In the basic amps-voltage world yes that is true. When my batteries are down voltage will slowly raise to the set point. They start doing smart electronics type things. From Heart.
Battery Charging Completely recharging wet cell deepcycle batteries requires the battery voltage to be raised beyond what is known as the gassing point. This is the voltage at which the battery begins to bubble and gas is given off. If charging stops short of this point, sulfate is left on the plates and deterioration of the battery begins. The gassing point will vary with battery temperature. At 77 degrees F, the gassing point of a 12 Volt battery is about 14.0 Volts.
Battery charging without excessive gassing of the batteries is accomplished with three-stage chargers. The Freedom Inverter/Charger utilizes this technique. Gel cell batteries must not be charged to their gassing point. In fact, high voltage charging which gasses these batteries is harmful to them. They typically require a lower bulk charge voltage and a higher float voltage than wet cell batteries. Consult the battery manufacturer for specifications. Conventional Battery Chargers Most conventional battery chargers are single-stage constant voltage chargers. They must stop short of the gassing point or they will overcharge the battery bank.
Most 12 Volt battery chargers bring the battery voltage up to about 13.8 Volts.
This presents two problems. First, since the battery voltage does not reach the gassing point, sulfate is left on the plates. Second, 13.8 Volts is close enough to the gassing point that some gas will escape, and the wet cell battery will need to be frequently topped off with distilled water. Conventional battery chargers also suffer from another inherent characteristic of design, which is a tapering effect. While they will deliver their rated current into a deeply discharged battery, as the battery voltage rises, the output current of the charger tapers down. This taper continues as the battery is charged, taking a very long time to reach an acceptable recharge level.
Freedom Battery Chargers Freedom battery chargers are designed to overcome the limitations of conventional chargers by utilizing 3 distinct stages, each designed for optimal recharging of both wet cell and gel cell deep-cycle batteries. Battery type selection is only available through the Freedom Remote Control Panel or a Link Instrument. Refer to the Freedom Remote Control Panel Addendum, pages 28-34, or a Link Owner’s ManualThe battery charger stages are:
Stage 1 - Bulk Charge During the bulk charge stage most of the charge is delivered to the battery bank. This phase is engaged as soon as the battery charger is activated. Full rated charger current is delivered to the battery bank until the bulk charge voltage limit is reached. This results in a relatively rapid recharge. Generally, a wet cell battery bank should not be charged up to the gassing point at a rate which exceeds 25% of its capacity. Example, a 12 Volt battery bank of 520 Amp-hours should not be charged at over 130 Amps.
Gel cell and Advanced AGM batteries can accept a higher rate of charge. Consult the manufacturer for specifications.
Stage 2 - Acceptance Charge The acceptance stage immediately follows the bulk charge stage. During this stage the battery voltage is held constant at the bulk charge voltage limit and the current gradually ramps down. During this stage the battery is accepting its final amount of charge current and the last of the sulfate on the plates is removed. The acceptance stage lasts until the charge current reaches the transition point in Amps. A timer will terminate the acceptance stage if this current level is not reached. The time is automatically set when the dip switches for battery type are set on the Freedom Remote Control Panel. Maximum acceptance time is 1 hour for wet cells and 3 hours for gel cells. Gel cell acceptance time can be longer because they are less likely to gas. Expect wet cell batteries to gas somewhat during acceptance, this is a necessary part of the charging process. NOTE: Acceptance timers are not used when Link Instruments control the charger. Refer to the Link Owner’s Manual.
Stage 3 - Float Charge When the acceptance stage is terminated, either because the charge current ramped down to the transition point or the timer engaged, charge current will shut off. The unit monitors the battery voltage while it drifts down from the bulk charge voltage limit. When it reaches the float voltage set point, the float charge stage is engaged. 14 The float charge stage holds the battery voltage at a lower level, where it is safe for long term battery maintenance. During the float charge stage, the full output current of the battery charger is available to operate any DC appliances that may be on the system, while constantly maintaining the float charge voltage. The battery charger remains in the float charge stage indefinitely until the charger is disconnected from incoming AC power or turned OFF with the Freedom Remote Control Panel or Link Instrument. ACCEPTANCE TO FLOAT TRANSITION POINTS Freedom 10-12V Freedom 10-24V Freedom 15-12V Freedom 20-12V Freedom 20-24V Freedom 20-32V Freedom 25-12V Freedom 25-24V 5 Amps DC 2.5 Amps DC 10 Amps DC 15 Amps DC 7.5 Amps DC 6 Amps DC 21 Amps DC 10 Amps DC
Stage 4 - Equalizing Charge This is the only battery charger stage which is not engaged automatically. It must be manually initiated each time it is necessary to equalize using a dip switch on the back of the Freedom Remote Control or the front panel on the Link Instrumentation. Applying an equalizing charge is not possible without the use of a Freedom Remote Panel or Link Instrument. Periodic equalizing is recommended by most wet cell deep-cycle battery manufacturers. There are no firm rules for how often an equalizing charge should be applied, but once a month is a good rule of thumb for batteries which are regularly cycled, less often f