SWC, you have two ways to get the power from these generators. The first being the usual duplex outlet on the front panel which is run through the 20A breaker also on the front panel. The second source is the banana plugs. If you just plug something into one generator using the duplex outlet you will be able to draw 13. 3 amps continous, the built-in breaker never coming into play because the internal regulation controls overloading such as drawing more than the 1600VA. You can draw up to 2000VA peak but only for a short time.
Now if you use the banana plugs they bypass the 20A breaker but you still can only pull the 13. 3 from one generator. Now here is the cool part. If you use the banana plugs and link hot to hot and neutral to neutral using SHIELDED! banana plugs you now can draw up to 20A from a pair of generators by plugging into only one of them because the slave makes up the difference between the 13. 3 and the 20A that the breaker allows.
Now if you add a 30A plug that is connected to the banana plug wires, tee off them as you stated, you can draw the full 26. 6A from only one plug, the 30A plug. The difference is that you can use one outlet to power a higher load as opposed to using the duplex outlets on the pair to power several lower power loads. It supplies the total of the two generator outputs to a single higher amp outlet.
You should respect anything that has the potential to kill you. You can use a suicide cord that has two male plugs on it and just plug the two generators together and it is the same as the banana plugs except that it still goes through the 20 breaker and also if it gets unplugged while the two are running someone can be killed by the exposed ends. This is why it is important to use SHIELDED banana plugs which have the internal metal tip covered by an insulator.
Now if you use the banana plugs they bypass the 20A breaker but you still can only pull the 13. 3 from one generator. Now here is the cool part. If you use the banana plugs and link hot to hot and neutral to neutral using SHIELDED! banana plugs you now can draw up to 20A from a pair of generators by plugging into only one of them because the slave makes up the difference between the 13. 3 and the 20A that the breaker allows.
Now if you add a 30A plug that is connected to the banana plug wires, tee off them as you stated, you can draw the full 26. 6A from only one plug, the 30A plug. The difference is that you can use one outlet to power a higher load as opposed to using the duplex outlets on the pair to power several lower power loads. It supplies the total of the two generator outputs to a single higher amp outlet.
You should respect anything that has the potential to kill you. You can use a suicide cord that has two male plugs on it and just plug the two generators together and it is the same as the banana plugs except that it still goes through the 20 breaker and also if it gets unplugged while the two are running someone can be killed by the exposed ends. This is why it is important to use SHIELDED banana plugs which have the internal metal tip covered by an insulator.