50 amp RV service uses 4 each #6 leads - 2 hots, each capable of 120VAC and 50 amps, 1 neutral and 1 ground. It is essential that the 2 hot legs be wired 180* out of phase to avoid excessive neutral leg currents. If these hot legs are 180* out of phase, a voltmeter will show 240VAC across the 2 hot legs and 120VAC from either hot leg to neutral. With the hot legs 180* out of phase, the neutral leg current is effectively the
difference between the hot leg currents; if the hot legs are in phase, the neutral leg current is effectively the
sum of the hot leg currents - if each hot leg were carrying 45 amps, the neutral current would be 0 amps if the hot legs were wired correctly, but 90 amps if the hot legs were miswired, thus overloading the #6 neutral lead.
Therefore, an RV with 50 amp service has a theoretical ampacity of 100 amps (2 each hot legs times 50 amps per leg) versus an ampacity of 30 amps for an RV with 30 amp service which only utilizes 1 hot leg capable of 120VAC and 30 amps, 1 neutral and 1 ground.
If a 30 amp RV is plugged into 50 amp service, it picks up one of the 50 amp hot legs that is protected in the shore power box by a 50 amp breaker. The only protection against overcurrent for the 30 amp RV, therefore, is the 30 amp main breaker in the RV's power distribution panel.
Rusty