The grounding issues. Currently NEC (National Electric Code) requires that equipment be "grounded" back to the source of power. This "ground" must be of sufficent size that if the device should fail to "ground" enough current will flow to trip the breaker! strangely enough this can contribute to electrocutions, that is why we now have to install GFI's (Ground Fault Interupters) in wet locations.
Now let,s look at "BONDING" which is an electrical term which is often confused with "grounding" The bond on equipment is not designed nor intended to carry any portion of the normal currents during operation. Sometimes the bonding and the ground will operate as parallel paths or appear to. What "bonding" does do is create a "Zone of Equipotential" this protects YOU while a fault is in progress. Look at a bird sitting on a 34. 5KV wire, no big deal, no shock it just flys away. Over in China Electrical workers climb a silk rope (a very good insulator) and actually work on 1MV (1,000,000 volt) while it's energized. WOW!
Now bonding connects "everything" (the planet Earth) together with a low resistance path, Remember OHM's law? {{Low resistance=low voltage and high current}}. Voltage kills. The line is around 50 volts depending on the situation. High current trips breakers and blows fuses. good thing!
Your Miller Dialarc welder may be equipped with a high frequency arc start unit. The high freq is something like 10,000 Hz, this is radio! So if the case is not "earthed" the transmitter can broadcast your signal! So the "grounding rod" requested by the manufacturer is required by the FCC (Federal Communications Commission) to limit your ability to "jam" the airwaves. Another NO-NO is cables should not be hung up in loops, figure eights on the floor or not coiled at all is best.
Truth is stranger than fiction!
Rich
------------------
2001. 5 2500 ETH/DEE 4x4,Patriot Blue over Silver,Camper pkg, Trailerpkg,3. 54LSD, Agate Leather,Stainless Smitty Bars,Tow hooks,Amsoil... ... ...

Except snowplow!