Folks,
I was intrigued by Darren’s My RV Works video on testing your propane system so I made my own test rig. I chose to remove the WH burner to make attaching the test rig easier. The locked PSI and loaded testing went well but the leak down, not so good.
During the leak down test, I could watch the pressure slowly drop, now time to find the leak. I soap bubbled from the tanks, regulator, hose, copper line and all fittings including the stove.
No bubbles found and I had no know propane leak symptoms.
Next, I decided to disconnect each appliance service line and plug the line. Re-pressurize and leak down test for each of them. Stove and refrigerator, no change and the WH burner was already disconnected. That left the furnace.
I’ve had the furnace burner out for service, not difficult to do. Then I capped the furnace line and leak tested. No more leak down pressure loss.
Next, I attached the burner and valve to my test line and turned on the propane. With soapy water on my finger tip the burner orifice blew bubbles. Order new valve, transfer the old parts to new valve, install and test. The leak down test was easily passed with the new valve.
If you’ve never had your rigs propane system leak down tested, might want to consider it as a maintenance item.
Please be careful if you decide to try working on your own propane system might be time to have your shop do this test.
Gary
I was intrigued by Darren’s My RV Works video on testing your propane system so I made my own test rig. I chose to remove the WH burner to make attaching the test rig easier. The locked PSI and loaded testing went well but the leak down, not so good.
During the leak down test, I could watch the pressure slowly drop, now time to find the leak. I soap bubbled from the tanks, regulator, hose, copper line and all fittings including the stove.
No bubbles found and I had no know propane leak symptoms.
Next, I decided to disconnect each appliance service line and plug the line. Re-pressurize and leak down test for each of them. Stove and refrigerator, no change and the WH burner was already disconnected. That left the furnace.
I’ve had the furnace burner out for service, not difficult to do. Then I capped the furnace line and leak tested. No more leak down pressure loss.
Next, I attached the burner and valve to my test line and turned on the propane. With soapy water on my finger tip the burner orifice blew bubbles. Order new valve, transfer the old parts to new valve, install and test. The leak down test was easily passed with the new valve.
If you’ve never had your rigs propane system leak down tested, might want to consider it as a maintenance item.
Please be careful if you decide to try working on your own propane system might be time to have your shop do this test.
Gary